Short Answer
Loads, such as heating and air-conditioning, that do not operate at the same time are said to be non-coincident loads. While separate circuits must be designed to serve each load, when calculating service load per NEC 220.60, only the ____________________ of two non-coincident loads need to be included.
Correct Answer: